1
Engineering Forum: experiences from cooling systems for LHC detectors
Bart VerlaatNational Institute for Subatomic Physics
(NIKHEF)Amsterdam, The Netherlands
CO2 cooling experiences in the LHCb Velo Thermal Control System
CERN, 30 October 2008
2
Table of Contents
• CO2 cooling and the 2PACL method
• LHCb-VELO Thermal Control System (VTCS).
• Commisioning results of the VTCS.
• Conclusions.
[email protected]@NIKHEF.NL
3
Why Evaporative CO2 Cooling?The lightest way of cooling is:
Evaporate at high pressure!
Why?Vapor expansion is limited under high pressure
Volume stays low
Pipe diameter stays low
Carbon Dioxide
High latent heat
Low mass flow
[email protected]@NIKHEF.NL
Mass stays low
dP/P is small
4
75
50
25
00 20 40-20-40-60
Temperature (°C)
Pre
ssu
re (
Ba
r)
Saturation curves in the PT Diagram for CO2, C2F6 & C3F8
(3 used or considered refrigerants at CERN)
CO2
C2F6
C3F8
[email protected]@NIKHEF.NL
5
Property comparison
Refrigerant “R” numbers:R744=CO2
R218=C3F8
R116=C2F6
-40 -30 -20 -10 0 10 200
0.05
0.1
0.15
0.2
0.25
0.3
0.35
0.4
DratioR744
DratioR218
DratioR116
Density Ratio (ρvapour/ ρliquid)
Saturation Temperature (ºC )
ρva
po
ur/
ρliq
uid
Be
tte
r
-40 -30 -20 -10 0 10 200
0.002
0.004
0.006
0.008
0.01
0.012
0.014
SurfTR744
SurfTR218
SurfTR116
Surface Tension
Saturation Temperature (ºC )
Sur
face
Ten
sion
(N
/m)
Be
tte
r
-40 -30 -20 -10 0 10 200.5
1
1.5
2
2.5
3
3.5
4
4.5
5x 10
-4
DVliqR744
DVliqR218
DVliqR116
Liquid Viscosity
Saturation Temperature (ºC )
Liqu
id V
isco
sity
(P
a*s)
Be
tte
r
-40 -30 -20 -10 0 10 200
50
100
150
200
250
300
350
dHR744
dHR218
dHR116
Latent Heat of Evaporation
Saturation Temperature (ºC )
Late
nt h
eat
of e
vapo
ratio
n (k
J/kg
)
Be
tte
r
-40 -30 -20 -10 0 10 200
5
10
15
20
25
dT/dP
Saturation Temperature (ºC )
dT/d
P (
ºC/b
ar) Be
tte
r
6
2 evaporative cooling principles used in LHC detectors
DetectorCooling plant
Warm transfer
Chiller Liquid circulationCold transfer
LHCb-VELO:
Atlas Inner Detector: Vapor compression systemFluid: C3F8
2PACL pumped liquid systemFluid: CO2
Hea
terCompressor
Pump
Compressor
BP. Regulator
Liquid Vapor
2-phase
Pre
ssur
e
Enthalpy
Liquid Vapor
2-phase
Pre
ssu
reEnthalpy
DetectorCooling plant
[email protected]@NIKHEF.NL
7
The 2-Phase Accumulator Controlled Loop (2PACL)
2PACL principle ideal for detector cooling:
- Liquid overflow => no mass flow control
- Low vapor quality => good heat transfer
- No local evaporator control, evaporator is passive in detector
- Very stable evaporator temperature control at a distance (P4-5 = P7)
Con
dens
er
PumpHeat exchanger
evaporatorRestrictor2-Phase
Accumulator
Hea
t in
Hea
t in
Hea
t out
Hea
t out
1
2 34
5
6
Liquid Vapor
2-phase
Enthalpy
Pre
ssu
re1
2 3
45
6P7
P7P4-5
[email protected]@NIKHEF.NL
Long distance
8
Electron
HadronProton beam
Proton beam
LHCb Detector Overview
Muon
LHCb Cross sectionGoals of LHCb:Studying the decay of B-mesons to find evidence of CP-violation(Why is there more matter around than antimatter?)
20 meter
Vertex Locator
[email protected]@NIKHEF.NL
9VELO Thermal Control System CO2 evaporator section
Detectors and electronics
23 parallel evaporator stations
capi
llarie
s
and
retu
rn h
ose
•Temperature detectors: -7ºC •Heat generation: max 1600 W
The LHCb-VELO Detector (VErtex Locator)
[email protected]@NIKHEF.NL
10
Particle tracks in the VELO from an LHC injection test (22 august ’08)
The Velo Detector
Heat producing electronics
CO2 evaporator(Stainless steel tube casted in aluminum)
Detection Silicon
[email protected]@NIKHEF.NL
11
VELO Cooling Challenges
• VELO electronics must be cooled in vacuum.– Good conductive connection– Absolute leakfree
• Maximum power of the electronics: 1.6 kW
• Silicon sensors must stay below -7°C at all times (on or off).
• Adjustable temperature for commisioning.– -5°C to -30°C in vacuum (Nominal -25°C)– +10°C to-10°C under Neon vented condition
• Maintenance free in (inaccessable) detector area
[email protected]@NIKHEF.NL
12
VTCS Evaporator
23 parallel evaporator stationsinner=1mm (L~1.5m)
Inlet capillariesinner=0.5mm (L~2m)
Aluminium casted evaporator block details
vacuum feed through
capillariesand return
hoseliquid inlet (¼”x0.035”)
2-phase outlet (⅜”x0.035”)
PT100 cables
13
4 m
2.6
m
2 R507A Chillers:1 water cooled1 air cooled
2 CO2 2PACL’s:1 for each detector half
55 m
Accessible and a friendly environment
Inaccessible and a hostile environment
2 Evaporators 800 Watt max per detector half
VELO
LHCb-VTCS Overview(VELO Thermal Control System)
[email protected]@NIKHEF.NL
PLC
2 Concentric transfer lines
4m th
ick
conc
rete
shi
eldi
ng w
all
14
Concentric transfer line
Ø4mm
Ø6mmØ14mm
Ø16mm
Ø66mm
Sub-cooled liquid feed line
2-phase return line
25mm Armaflex NH Isolation
Protective cover
Transfer line is a 55m long concentric 2-fase liquid-vapor line
Functions:•Transferring liquid to evaporators•Regulate liquid temperature•Pick up environmental heat in return line for unloaded evaporator cooling
•Provide low-pressure drop return flow for distant evaporator pressure control
Terminals as built
VTCS total upward column: 4m+2.6m = 6.6mΔT ≈ 0.7°C → ≈ 0.1°C/m (C3F8 ≈ 2.3°C/m)
2.6m
4m
15
VTCS Accumulator Control
Thermo siphon heater for pressure increase(Evaporation)
Cooling spiral for pressure decrease(Condensation)
Accumulator properties:• Volume: 14.2 liter (Loop 9 Liter)• Heater capacity: 1 kW• Cooler capacity: 1 kW• System charge: 12 kg (@23.2 liter)• System design pressure: 135 bar
[email protected]@NIKHEF.NL
++
+_+
_
Heating
Cooling
Set point Temperature
Temperature
Pre
ssur
e
Evaporator Pressure
Pressure drop
PIDPset
Tset
Paccumulator
ΔPfault
16
VTCS Schematics2x CO2 2PACL’s connected to 2 R507A chillers
(Redundancy)
Lots of sensors and valves
TR_AC101
TR_PM101
Tertiary VTCS Right Detector (TR)
TR_PT101TR_PT104
TR_PT102
TR_VL101
TR_VL103
TR_VL104 TLR_VL105
TR_VL106
TR_VL107
TR_VL108
TR_VL109
TR_VL110
TR_VL111
TR_VL113
TR_LT101
TR_BD103
SA_HX105 / TR_HX101 SB_HX105 /
TR_HX102
SA_HX108 / TR_HX103
TL_HT103
TR_HT104
SB_HX108 / TR_HX104
TR_HT101
TR_VL102
TR_PT103TR_HT102
TR_BD101
TR_BD102
TR_BD104
TR_BD106
TR_BD107
TLR_VL101
TLR_PM101
TLR_VL107
TLR_VL109
TLR_VL110
TLR_VL111
Liquid to concentric tube
Vapor mixture from concentric tube
Vapor mixture from concentric tube
Liquid to concentric tube
TL_AC101
TL_PM101
Tertiary VTCS Left Detector (TL)
TL_PT101TL_PT104
TL_PT102
TL_VL101
TL_VL103
TL_VL104TL_VL105
TL_VL106
TL_VL107
TL_VL108
TL_VL109
TL_VL110
TL_VL111
TL_VL113
TL_LT101
TL_BD103
SA_HX103 / TL_HX101
SB_HX103 / TL_HX102
SA_HX107 / TL_HX103
TL_HT103
TL_HT104
SB_HX107 / TL_HX104
TL_HT101
TL_VL115
TL_VL102
TL_PT103TL_HT102
TL_BD101
TL_BD102
TL_BD104
TL_BD106
TL_BD107
TLR_PT103
TLR_HT102
(101)
(103) (104)
(106)
(105)
(112)
(115)
(116)
(117)
(118)
(121)
(123)
(122) (114)
(113)
(120)
(107)
(102) (119)
(110)
(108)
(109)
(101)
(103) (104)
(106)(105)
(111)
(112)
(115)
(116)
(117) (118)
(121)
(123)
(122)(114)
(113)
(120)
(107)
(110)
(108)
(109)
(124) (124)
(112)
(115)
(122)
(114)
(113)
TL_VL112 TR_VL112
TL_HT105
(125)
TR_HT105(125)
TR_FL101
TL_FL102 TR_FL102
TL_FL101
TR_HX105
(102) (119)
Tambient
TL_VL114
TLR_VL115
TR_VL115
TR_VL114
TLR_VL114
TL_S.01
S.02
S.04
S.05
S.03
S.15
S.16
S.17
S.19
S.18.01
S.18.02
S.09.29
S.20
S.21
S.22
S.23
TLR_S.20
TLR_S.01
TR_S.01
S.02
S.05
S.04
S.03
S.23
S.15
S.16
S.17
S.18.01 S.18.02
S.19
S.22
S.20
S.21
S.12.29S.09.29
S.12.29
TR_AC101
TR_PM101
Tertiary VTCS Right Detector (TR)
TR_PT101TR_PT104
TR_PT102
TR_VL101
TR_VL103
TR_VL104 TLR_VL105
TR_VL106
TR_VL107
TR_VL108
TR_VL109
TR_VL110
TR_VL111
TR_VL113
TR_LT101
TR_BD103
SA_HX105 / TR_HX101 SB_HX105 /
TR_HX102
SA_HX108 / TR_HX103
TL_HT103
TR_HT104
SB_HX108 / TR_HX104
TR_HT101
TR_VL102
TR_PT103TR_HT102
TR_BD101
TR_BD102
TR_BD104
TR_BD106
TR_BD107
TLR_VL101
TLR_PM101
TLR_VL107
TLR_VL109
TLR_VL110
TLR_VL111
Liquid to concentric tube
Vapor mixture from concentric tube
Vapor mixture from concentric tube
Liquid to concentric tube
TL_AC101
TL_PM101
Tertiary VTCS Left Detector (TL)
TL_PT101TL_PT104
TL_PT102
TL_VL101
TL_VL103
TL_VL104TL_VL105
TL_VL106
TL_VL107
TL_VL108
TL_VL109
TL_VL110
TL_VL111
TL_VL113
TL_LT101
TL_BD103
SA_HX103 / TL_HX101
SB_HX103 / TL_HX102
SA_HX107 / TL_HX103
TL_HT103
TL_HT104
SB_HX107 / TL_HX104
TL_HT101
TL_VL115
TL_VL102
TL_PT103TL_HT102
TL_BD101
TL_BD102
TL_BD104
TL_BD106
TL_BD107
TLR_PT103
TLR_HT102
(101)
(103) (104)
(106)
(105)
(112)
(115)
(116)
(117)
(118)
(121)
(123)
(122) (114)
(113)
(120)
(107)
(102) (119)
(110)
(108)
(109)
(101)
(103) (104)
(106)(105)
(111)
(112)
(115)
(116)
(117) (118)
(121)
(123)
(122)(114)
(113)
(120)
(107)
(110)
(108)
(109)
(124) (124)
(112)
(115)
(122)
(114)
(113)
TL_VL112 TR_VL112
TL_HT105
(125)
TR_HT105(125)
TR_FL101
TL_FL102 TR_FL102
TL_FL101
TR_HX105
(102) (119)
Tambient
TL_VL114
TLR_VL115
TR_VL115
TR_VL114
TLR_VL114
TL_S.01
S.02
S.04
S.05
S.03
S.15
S.16
S.17
S.19
S.18.01
S.18.02
S.09.29
S.20
S.21
S.22
S.23
TLR_S.20
TLR_S.01
TR_S.01
S.02
S.05
S.04
S.03
S.23
S.15
S.16
S.17
S.18.01 S.18.02
S.19
S.22
S.20
S.21
S.12.29S.09.29
S.12.29
[email protected]@NIKHEF.NL
17
VTCS construction• CO2 2PACL’s
– Stainless steel piping with:• (Orbital) Welding• Vacuum Brazing • Swagelok Cajon VCR fittings and line components
– Lewa liquid CO2 pump (100 bar)– In house designed accumulator (130 bar)– Reinforced SWEP condenser (130 bar)
• Now commercial available at SWEP.– 55 meter concentric transfer line– Aluminium casted cooling blocks– Test pressure 170 bar
• Chillers designed in house with standard commercial chiller components.– Copper piping with hard solder joints – Danfoss line components– Bitzer compressors– SWEP heat exchangers
• Siemens S7-400 series Programmable Logic Controller (PLC)
[email protected]@NIKHEF.NL
18
LHCb-VTCS Cooling Plant
Pumps
Accumulators
Valves
[email protected]@NIKHEF.NL
CondensersCO2 2PACL systems
Freon chiller systems
19
VTCS Units Installed @ CERN
July- August 2007
CO2 Unit
Freon Unit
20
13 13.5 14 14.5 15 15.5
-100
-75
-50
-25
0
25
50
75
Clock time (hour)
Tem
pera
ture
(°C
) P
ress
ure
(B
ar)
Leve
l (%
)C
oolin
g/H
eatin
g P
ow
er (%
kW)
VTCS 2PACL Operation From start-up to cold operation (1)
2 Pump head pressure (Bar)
4 - Accumulator pressure (Bar)
1 Pumped liquid temperature (°C)
5 – Evaporator temperature (°C)
4-Accumulator liquid level (vol %)
4- Accumulator Control: + = Heating - = Cooling _
+
4
1
2
7
7
7
7
1
2
7
4
+7
-7
[email protected]@NIKHEF.NL
21
AccumulatorCooling
= Pressure decrease
13 13.5 14 14.5 15 15.5-50
-25
0
25
50
75
Clock time (hour)
Tem
pera
ture
(°C
)
Pre
ssure
(B
ar)
VTCS 2PACL Operation From start-up to cold operation (2)
AB
C
D2 - Pump head pressure (Bar)
4 - Accumulator pressure (Bar)
1 – Pumped liquid temperature (°C)
5 – Evaporator temperature (°C)
50 100 150 200 250 300 350 4005x100
101
102
2x102
h [kJ/kg]
P [bar]
-40°C
-20°C
0°C
20°C
40°C
0.2 0.4 0.6 0.8
VTCS start-up and operating cycles
1
3,5
810,13
1
3 5
8
9,10,13
1
35
8
9,10131
3 5
8
9 10 13
CB
D E
A
50 100 150 200 250 300 350 4005x100
101
102
2x102
h [kJ/kg]
P [bar]
-40°C
-20°C
0°C
20°C
40°C
0.2 0.4 0.6 0.8
VTCS start-up and operating cycles
1
3,5
810,13
1
3 5
8
9,10,13
1
35
8
9,10131
3 5
8
9 10 13
CB
D E
A
20 °C
0 °C
-20 °C
-40 °C
1
2
4
A
BC
D Path of 54
41
2
5
2
5
4
1
5
5
Enthalpy
Pre
ssu
re
Set-point range
[email protected]@NIKHEF.NL
22
March ’08: Commisioning of the VTCSDetector under vacuum and
unpowered
10 15 20 25 30 35 40 45 50 55 60 65 70-50
-45
-40
-35
-30
-25
-20
-15
-10
-5
0
5
10
15
20
25
30
Time from 29 March clock time (Hours)
Mea
sure
d Te
mpe
ratu
re (º
C)
C-Side CO2 Cooling System Performance During Detector Vacuum Tests(29 march 08 - 31 March 08)
Accumultor saturation temperature (TRPT102tsat) = SetpointTR Evaporator Temperature (TRTT048pvss)
Condenser Inlet (TRTT101pvss)
Condenser Out- / Pump Inlet Temperature (TRTT112pvss)
Pump Outlet Temperature (TRTT120pvss)
C-Side RF-Foil temperature (TRTT043pvss)C-Side Module Base Temperature (TRTT038pvss)
Sp=-10ºC
Sp=-20ºC
Sp=-30ºC
Sp=0ºC
Sp=-25ºC
Sp=-30ºC
Sp=0ºC
2 Days + 6 hours cooling under vacuum at several set point temperatures
Start-up
10 15 20 25 30 35 40 45 50 55 60 65 70-50
-45
-40
-35
-30
-25
-20
-15
-10
-5
0
5
10
15
20
25
30
Time from 29 March clock time (Hours)
Mea
sure
d Te
mpe
ratu
re (º
C)
C-Side CO2 Cooling System Performance During Detector Vacuum Tests(29 march 08 - 31 March 08)
Accumultor saturation temperature (TRPT102tsat) = SetpointTR Evaporator Temperature (TRTT048pvss)
Condenser Inlet (TRTT101pvss)
Condenser Out- / Pump Inlet Temperature (TRTT112pvss)
Pump Outlet Temperature (TRTT120pvss)
C-Side RF-Foil temperature (TRTT043pvss)C-Side Module Base Temperature (TRTT038pvss)
Sp=-10ºC
Sp=-20ºC
Sp=-30ºC
Sp=0ºC
Sp=-25ºC
Sp=-30ºC
Sp=0ºC
2 Days + 6 hours cooling under vacuum at several set point temperatures
Start-up
Sp=-10ºC
Sp=-20ºC
Sp=-30ºC
Sp=0ºC
Sp=-25ºC
Sp=-30ºC
Sp=0ºC
2 Days + 6 hours cooling under vacuum at several set point temperatures
Start-up
10 15 20 25 30 35 40 45 50 55 60 65 70-50
-45
-40
-35
-30
-25
-20
-15
-10
-5
0
5
10
15
20
25
30
Time from 29 March clock time (Hours)
Measure
d Temp
erature
(ºC)
C-Side CO2 Cooling System Performance During Detector Vacuum Tests(29 march 08 - 31 March 08)
Accumultor saturation temperature (TRPT102tsat) = Setpoint
TR Evaporator Temperature (TRTT048pvss)
Condenser Inlet (TRTT101pvss)
Condenser Out- / Pump Inlet Temperature (TRTT112pvss)
Pump Outlet Temperature (TRTT120pvss)
C-Side RF-Foil temperature (TRTT043pvss)
C-Side Module Base Temperature (TRTT038pvss)
Sp=-10ºC
Sp=-20ºC
Sp=-30ºC
Sp=0ºC
Sp=-25ºC
Sp=-30ºC
Sp=0ºC
2 Days + 6 hours cooling under vacuum at several set point temperatures
Start-up
10 15 20 25 30 35 40 45 50 55 60 65 70-50
-45
-40
-35
-30
-25
-20
-15
-10
-5
0
5
10
15
20
25
30
Time from 29 March clock time (Hours)
Measure
d Temp
erature
(ºC)
C-Side CO2 Cooling System Performance During Detector Vacuum Tests(29 march 08 - 31 March 08)
Accumultor saturation temperature (TRPT102tsat) = Setpoint
TR Evaporator Temperature (TRTT048pvss)
Condenser Inlet (TRTT101pvss)
Condenser Out- / Pump Inlet Temperature (TRTT112pvss)
Pump Outlet Temperature (TRTT120pvss)
C-Side RF-Foil temperature (TRTT043pvss)
C-Side Module Base Temperature (TRTT038pvss)
Sp=-10ºC
Sp=-20ºC
Sp=-30ºC
Sp=0ºC
Sp=-25ºC
Sp=-30ºC
Sp=0ºC
2 Days + 6 hours cooling under vacuum at several set point temperatures
Start-up
Sp=-10ºC
Sp=-20ºC
Sp=-30ºC
Sp=0ºC
Sp=-25ºC
Sp=-30ºC
Sp=0ºC
2 Days + 6 hours cooling under vacuum at several set point temperatures
Start-up Condenser outlet / Pump sub cooling Pump outlet RF-foil
10 15 20 25 30 35 40 45 50 55 60 65 70-50
-45
-40
-35
-30
-25
-20
-15
-10
-5
0
5
10
15
20
25
30
Time from 29 March clock time (Hours)
Measure
d Temp
erature
(ºC)
C-Side CO2 Cooling System Performance During Detector Vacuum Tests(29 march 08 - 31 March 08)
Accumultor saturation temperature (TRPT102tsat) = Setpoint
TR Evaporator Temperature (TRTT048pvss)
Condenser Inlet (TRTT101pvss)
Condenser Out- / Pump Inlet Temperature (TRTT112pvss)
Pump Outlet Temperature (TRTT120pvss)
C-Side RF-Foil temperature (TRTT043pvss)
C-Side Module Base Temperature (TRTT038pvss)
Sp=-10ºC
Sp=-20ºC
Sp=-30ºC
Sp=0ºC
Sp=-25ºC
Sp=-30ºC
Sp=0ºC
2 Days + 6 hours cooling under vacuum at several set point temperatures
Start-up
10 15 20 25 30 35 40 45 50 55 60 65 70-50
-45
-40
-35
-30
-25
-20
-15
-10
-5
0
5
10
15
20
25
30
Time from 29 March clock time (Hours)
Measure
d Temp
erature
(ºC)
C-Side CO2 Cooling System Performance During Detector Vacuum Tests(29 march 08 - 31 March 08)
Accumultor saturation temperature (TRPT102tsat) = Setpoint
TR Evaporator Temperature (TRTT048pvss)
Condenser Inlet (TRTT101pvss)
Condenser Out- / Pump Inlet Temperature (TRTT112pvss)
Pump Outlet Temperature (TRTT120pvss)
C-Side RF-Foil temperature (TRTT043pvss)
C-Side Module Base Temperature (TRTT038pvss)
Sp=-10ºC
Sp=-20ºC
Sp=-30ºC
Sp=0ºC
Sp=-25ºC
Sp=-30ºC
Sp=0ºC
2 Days + 6 hours cooling under vacuum at several set point temperatures
Start-up
Sp=-10ºC
Sp=-20ºC
Sp=-30ºC
Sp=0ºC
Sp=-25ºC
Sp=-30ºC
Sp=0ºC
2 Days + 6 hours cooling under vacuum at several set point temperatures
Start-up Accumulator saturation (Set-point) Evaporator temperature Condenser inlet
[email protected]@NIKHEF.NL
2316.5 17 17.5 18 18.5
-40
-20
0
20
40
60
80
Clock time (Hour)
Tem
pera
ture
('C)
, Liq
uid
leve
l (vo
l %),
Powe
r (%
kW o
r Wat
t)
Total C detector load (% kW)Evaporator Temperature ('C)Accumulator Liquid Level (vol %)Acumulator heating/cooling (% kW)Module VL11-C power (Watt)Module VL11-C cookie temperature ('C)Module VL11-C NTC00 temperature ('C)Module VL11-C NTC01 temperature ('C)
SP=-25°C
SP=-5°C
(3 sept 08)
[email protected]@NIKHEF.NL
Accu level
Module Heat load
Silicon temperature
Evaporator temperature
Accu Heating/Cooling
24 June ’08: After a succesful commisioning of the detector at -25°C, the setpoint is increased to -5°C.
And has been running since then smoothly!
80
60
40
20
0
-20
-400 0:30 1:00 1:30 2:00
Time (Hour)Te
mp
era
ture
(°C
), P
ower
(W
att)
, Le
vel (
vol %
)
Detector half heat load (x10)
-7°C
24
CO
2 li
quid
dT=
4.5
°CC
oolin
g bl
ock
dT=
0.0
4°C
1 hour
Evaporator Pressure 31.15 bar = -4.18°C
Cooling block temperature = -2.8°C
CO2 liquid temp= -42°C
Evaporator liquid inlet temp = -4.40°C
Evaporator vapor outlet temp = -4.44°C
Accumulator Pressure 30.54 bar = -4.90°C
Det
ect
or o
ffse
t fr
om a
ccu
cont
rol:
0.7
°CCO2 heat transfer dT=1.4°C
VTCS performance overview for a setpoint of -5°C (Detector switched on, fully powered)[email protected]@NIKHEF.NL
dP=
0.6
bar
= 6
.2 m
sta
tic h
eigt
h
Fluctuations from the untuned chiller
25
Summary
• The VTCS has successfully passed the 1st commissioning phase and was ready to be used in the experiment in July 2008
• Operational temperature range is between -5°C and -30°C set point for the water cooled chiller
• It has run for 3½months continuously with only minor problems
• It behaves very stable with the chiller still to be tuned (evaporator stability less than 0.05°C)
• The silicon temperature is below the required -7°C @ -25°C set point temperature. (This is consistent with the prediction)
[email protected]@NIKHEF.NL
26
What did we learn:
• 2PACL dynamics work better with the accumulator connection at inlet of condenser (instead of outlet as it is now)– No saturated liquid feed from accu to pump.– Free pre-cooling at cold start-up due to thermal
capacity of condensers.
• Concentric transfer tube heat exchanger works beyond expectations as the so-called “Duck-foot-cooling1” pinciple is boosting the operational temperature range.
• The current system is not always initiating boiling at higher operational temperatures (>-10°C), resulting in temporary reduced heat-exchange.
1 The way a duck can have cold feet without loosing body heat, by exchanging heat between the in- and outlet bloodstream.
27
The “Cool” future
• The VTCS is not yet finnished, some things have to be done:– Implementing automatic back-up procedure.– Changing the accumulator connection.– Tunning the chiller.– Analyse data for publication.
• Construction of a mini desktop 2PACL CO2 circulator for general purpose laboratory use.
• Participation in future CO2 cooling systems – Atlas IBL, Goat, Next-64, RELAXed
• 2PACL upgrade:– Replace HFC chiller by CO2 chiller
• No integration of chiller and 2PACL!– 2PACL is much more stable (<0.05’C)– 2PACL has liquid overfeed and needs no boil-off heaters– CO2 compressor needs oil as lubricant
• CO2 chiller has extended lower temperature range (CO2 ~-50°C , HFC~-40°C )
28
Back-up Slides
29
Property Comparison (1)R744 (CO2)
R116 (C2F6)
R218 (C3F8)
Source Refprop NIST
R744 (CO2)
R218 (C3F8)
R116 (C2F6)
Critical Point
31ºC @ 73.8 bar
71.9ºC @26.4 bar
19.9ºC @30.5 bar
Triple point -56.6ºC -147.7ºC -100ºC
Boiling temperature @ 1 bar
-78.4ºC Subli-mation !
-36.8ºC -78.1ºC
30
2 3 4 5 6 7 8 9 10-5
-4.5
-4
-3.5
-3
-2.5
-2
-1.5
-1
-0.5
0
Hydraulic Diameter (mm)
Pres
sure
Dro
p (b
ar)
2 3 4 5 6 7 8 9 10-10
-9
-8
-7
-6
-5
-4
-3
-2
-1
0
Hydraulic Diameter (mm)
Tem
pera
ture
Dro
p (º
C)
CO2 =2.7mm
2 3 4 5 6 7 8 9 10-5
-4.5
-4
-3.5
-3
-2.5
-2
-1.5
-1
-0.5
0
Hydraulic Diameter (mm)
Pres
sure
Dro
p (b
ar)
C2 F
6 =4.3mm
C3 F
8 =7.7mm
ΔT=-2°C
2x 20 wafers à 17 Watt
1 Atlas stave : 2 meter length
Cooling
Q = 680 WattTube = 4 meter
Example of and Atlas upgrade stave (1)
CO 2
C 3F 8
C2F 6
CO 2
C 3F 8
C2F 6
Calculations based on -35°C and 75% vapor quality at exit
Mass flow @ -35ºC Φ CO2= 2.9 g/s
Φ C3F8= 8.7 g/s
Φ C2F6= 9.6 g/s
Pressure Drop
Temperature Drop
Generates
31
•7.7
0 0.5 1 1.5 2 2.5 3 3.5 40
5000
10000
15000
Tube Length (m)
Hea
t Tra
nsfe
r C
oeffic
ient
(W
/m2K
)
0 0.5 1 1.5 2 2.5 3 3.5 4-36
-34
-32
-30
-28
-26
-24
-22
Tube length (m)
Tem
pera
ture
(°C
)
CO2
C3F8
C2F6
D2.7mm x L25mm = 80167 W/m2
D2.7mm x L75mm = 26722 W/m2
D4.3mm x L25mm = 50337 W/m2
D4.3mm x L75mm = 16779 W/m2
D7.7mm x L25mm = 28110 W/m2
D7.7mm x L75mm = 9370 W/m2
CO2
C3F8
C2F6
25mm HX length
75mm HX length
Example of and Atlas upgrade stave (2)
Mass flux @ -35ºC Φ’ CO2= 506 kg/m2s
Φ’ C3F8= 661 kg/m2s
Φ’ C2F6= 186 kg/m2s
Critical Heat Flux (Bowring/Ahmad): CHF(CO2) = 313 kW/m2, x=1.1
25mm
75mm
Heat exchange length