INTRODUCTIONS On-line Insulation condition monitoring of End-point Bonding cables Lulu Li, Jing Yong Department of Electrical and Computer Engineering, University of Alberta The increasing using of cables in power system has been followed by the growing of ageing cables. The unpredictable cable faults cause sudden blackout and pressing service for crews. Therefore, the on-line insulation condition monitoring has become an urgent demand for utilities. This work presents a new solution to achieve this goal based on power disturbances, in contrast to the status that an reliable online program that has not yet appeared. CHALLENGES NEW SOLUTION BASED ON POWER DISTURBANCES From a conventional view, the preferred on-line method will be to translate the mature off-line method Very-low Frequency Tanδ Measurement to on- line use. However, there are too many practical obstacles when apply it on-line, including: Additional very-low frequency source will bring an unexpectedly interference to power systems; GPS synchronization with very high precision is essential but unachievable and costly. This demand roots in the running condition of power cables, in contrast to the test condition of open circuit under off-line experiments. SIMULATION VERIFICATION ADVANTAGES FOR ON-LINE APPLICATION Power disturbances Subsation Z load i 2 i 1 u 2 Source PQM PQM End-point Bonding Cable Other feeders Other feeders Load switching Lightening stroke Faults Capacitor switching The magnitudes and distortions are distinct No additional interfere & possible utilizing Natural and frequent in power systems Abundant information in the transient waveform Can be easily captured by PQM Ideal ‘probe’ for cable insulation monitoring Basic idea The on-line insulation condition monitoring is implemented by analyzing the change trend of insulation parameters. The insulation parameters are estimated from the transients under each power disturbance events. The key part is the design of estimation model. Design of estimation model ( )=| + )( 2 + 1) + ( 2 − 1) + ( 2 −1 ( 2 + 1) + ( 2 − 1) + 2 |− | ) 1 ( | | ) 1 ( | Transient signal extraction Insulation parameters estimation (in frequency domain) Insulation conditions trend diagnosis Part 1 Part 2 Part 3 Power disturbances f(kHz) f(kHz) t(s) t(s) i 1 (kA) i 2 (kA) I 2 (A) I 1 (A) τ=5ms Disturbance occur Window 1 (a) (b) (c) (d) Window 2 f(kHz) f(kHz) t(s) t(s) i 1 (kA) i 2 (kA) I 2 (A) I 1 (A) τ=5ms Disturbance occur Window 1 (a) (b) (c) (d) Window 2 Cable conditions Power disturbances Capacitor switching No-load line switching Grounding fault Little aging 1.16% 1.24% 1.19% Aging 0.62% 0.85% 0.75% Serious aging 0.54% 0.05% 0.01% Damaged 0.05% 0.07% 0.07% f(kHz) f(kHz) t(s) t(s) i 1 (kA) i 2 (kA) I 2 (A) I 1 (A) τ=5ms Disturbance occur Window 1 (a) (b) (c) (d) Window 2 No additional interference to systems No need of GPS synchronization & phase angle Achievable monitor device PQM Estimation error Capacitor Switching Un-load Line Switching Grounding Fault To validate the advantage of the proposed method that no-need of signal GPS synchronization, an intentional time-delay (5ms ) is set between the sampling Window 1 and Window 2, the insulation parameters estimated by the proposed method is : the transient waveforms and amplitude spectrums: CONCLUSIONS A new application of power disturbances is explored to diagnose the insulation condition of end-point bonding cables on-line. The method is developed in frequency domain, which utilizes amplitude spectrums of the transients from PQM to estimate the insulation parameters. This method can do not rely on GPS synchronization and has no interface to power systems. The effectiveness of the proposed method is verified through a 5ms delay between two GPS devices. The estimation results, available measure requirements, and widely installed PQM all exhibit the prospect of on-line application of the proposed method in the future smart gird. In this model, and are impedance per unit of cable core and sheath, respectively; is the grounding resistance; is the variable containing the insulation parameters (relative complex permittivity) . The principle of the design of estimation model is making full use of amplitude spectrum. By this way, the power disturbances can be utilized to realize the monitoring with less hardware requirements, which benefit the on-line application. This estimation model is established on the analysis of cable model. A frequency-dependent distribution cable model is adopt, and the cable parameters as shown in the equation have the frequency dependent characters.

Transcript of On-line Insulation condition monitoring of End-point...

Page 1: On-line Insulation condition monitoring of End-point …apic/uploads/Forum/Pst14f2018.pdfINTRODUCTIONS On-line Insulation condition monitoring of End-point Bonding cables Lulu Li,

INTRODUCTIONS

On-line Insulation condition monitoring of End-point Bonding cables

Lulu Li, Jing Yong

Department of Electrical and Computer Engineering, University of Alberta

The increasing using of cables in power system has been

followed by the growing of ageing cables. The unpredictable

cable faults cause sudden blackout and pressing service for

crews. Therefore, the on-line insulation condition monitoring

has become an urgent demand for utilities.

This work presents a new solution to achieve this goal based

on power disturbances, in contrast to the status that an

reliable online program that has not yet appeared.

CHALLENGES

NEW SOLUTION BASED ON POWER DISTURBANCES

From a conventional view, the preferred on-line method will be to translate the mature off-line

method — Very-low Frequency Tanδ Measurement to on- line use. However, there are too many

practical obstacles when apply it on-line, including:

Additional very-low frequency source will bring an unexpectedly interference to power systems;

GPS synchronization with very high precision is essential but unachievable and costly.

This demand roots in the running condition of power cables, in contrast to the test condition of

open circuit under off-line experiments.

SIMULATION VERIFICATION

ADVANTAGES FOR ON-LINE APPLICATION

Power disturbances

Subsation

Zload

i2i1

u2

Source

PQM PQMEnd-point Bonding Cable

Other feeders

Other feeders

Load switching Lightening stroke

Faults

Capacitor switching

➢ The magnitudes and distortions are distinct

No additional interfere & possible utilizing➢ Natural and frequent in power systems

➢ Abundant information in the transient waveform

Can be easily captured by PQM

Ideal ‘probe’ for cable insulation monitoring

Basic idea

The on-line insulation condition monitoring is implemented by analyzing

the change trend of insulation parameters. The insulation parameters

are estimated from the transients under each power disturbance events.

The key part is the design of estimation model.

Design of estimation model

𝑀𝑖𝑛 𝐽(𝜀𝑟) = |𝑧𝑐 + 𝑧𝑠)(𝑒

2𝛾𝑙 + 1) + 𝑅𝑔𝛾(𝑒2𝛾𝑙 − 1) + 𝑍𝑙𝑜𝑎𝑑𝛾(𝑒

2𝛾𝑙 − 1

𝑧𝑠(𝑒2𝛾𝑙 + 1) + 𝑅𝑔𝛾(𝑒

2𝛾𝑙 − 1) + 2𝑧𝑐𝑒𝛾𝑙

| −| )𝐼1(𝑓 |

| )𝐼1(𝑓 |

Transient signal

extraction

Insulation parameters

estimation

(in frequency domain)

Insulation conditions

trend diagnosis

Part 1

Part 2

Part 3

Power disturbances

f(kHz)

f(kHz)

t(s)

t(s)

i 1 (k

A)

i 2 (k

A)

I 2 (A

)I 1

(A

)

τ=5ms

Disturbance occur

Window 1

(a) (b)

(c) (d)

Window 2

f(kHz)

f(kHz)

t(s)

t(s)

i 1 (k

A)

i 2 (k

A)

I 2 (A

)I 1

(A

)

τ=5ms

Disturbance occur

Window 1

(a) (b)

(c) (d)

Window 2

Cable conditions

Power disturbances

Capacitor switching

No-load line switching

Grounding fault

Little aging 1.16% 1.24% 1.19%

Aging 0.62% 0.85% 0.75%

Serious

aging0.54% 0.05% 0.01%

Damaged 0.05% 0.07% 0.07%

f(kHz)

f(kHz)

t(s)

t(s)

i 1 (k

A)

i 2 (k

A)

I 2 (A

)I 1

(A

)

τ=5ms

Disturbance occur

Window 1

(a) (b)

(c) (d)

Window 2

No additional interference to systems

No need of GPS synchronization & phase angle

Achievable monitor device — PQM

Estimation error

Cap

acit

or

Swit

chin

g

Un

-lo

ad L

ine

Sw

itch

ing

Gro

un

din

g Fa

ult

To validate the advantage of the proposed method that no-need

of signal GPS synchronization, an intentional time-delay (5ms )

is set between the sampling Window 1 and Window 2, the

insulation parameters estimated by the proposed method is :

➢ the transient waveforms and amplitude spectrums:

CONCLUSIONSA new application of power disturbances is explored to

diagnose the insulation condition of end-point bonding cables

on-line. The method is developed in frequency domain, which

utilizes amplitude spectrums of the transients from PQM to

estimate the insulation parameters. This method can do not

rely on GPS synchronization and has no interface to power

systems. The effectiveness of the proposed method is verified

through a 5ms delay between two GPS devices. The

estimation results, available measure requirements, and widely

installed PQM all exhibit the prospect of on-line application of

the proposed method in the future smart gird.

In this model, 𝑧𝑐 and 𝑧𝑠 are impedance per unit of cable core and sheath, respectively; 𝑅𝑔 is the

grounding resistance; 𝛾 is the variable containing the insulation parameters 𝜺𝒓 (relative

complex permittivity) .

The principle of the design of estimation model is making full use of amplitude spectrum. By this

way, the power disturbances can be utilized to realize the monitoring with less hardware

requirements, which benefit the on-line application. This estimation model is established on the

analysis of cable model. A frequency-dependent distribution cable model is adopt, and the cable

parameters as shown in the equation have the frequency dependent characters.