APEM Spring Forum
Meeting the Conservative
Challenges of the 21st Century
with
Magnetic Bearing Chillers
Introduction to Mag Bearing Chillers Since 2003
• Magnetic bearing chillers minimize efficiency losses and
mechanical complexity inherent to traditional centrifugal
chillers
Typical Performance Comparisons
0
0.2
0.4
0.6
0.8
1
20% 40% 60% 80% 100%
Percent Load
kW
/To
n
Frictionless Centrifugal W/C ScrewW/C Scroll Centf w/VFD
All Chillers at 150 Tons
Frictionless Compressor Benefits
• Efficient HFC-134a Design
– Part load performance as low as .325 kW/ton IPLV at ARI
• Quiet
– As low as 73 dBA per ARI Standard 575
– The pumps are louder than the chiller
• Low Maintenance Costs / Long Term Sustainability
– Eliminates the oil support system
Ideal for green buildings
County Office Building, Olathe KS
150-ton McQuay WMC Chiller installed
LEED Gold certified
• Magnetic Bearings have less than 0.2% the Friction Losses compared to Conventional Roller or Ball Bearing Designs
Why Magnetic Bearings?
compressor has permanent magnetic shaft and bearings,
position is “trimmed” with electromagnets.
Radial Bearings
10
• The Rotor Shaft Is Held in Position
With Electro Magnetic Cushions.
These Continually Change in Field
Strength to Keep the Shaft
Centrally Positioned. The Shaft’s
Position Is Monitored by 10 Sensor
Coils Whose Signals Are Fed Back
to a Digital Controller
• LRA = 2 amps
Magnetic Bearing Drive train
How does it work?
• 2-Stage
• Integral VFD – Speeds Up to 35,000 RPM
• Magnets Levitate Shaft and Impeller
• (2) Radial, (1) Axial Thrust
• Direct Drive 97% Efficient Synchronous Motor
• Capacitors Provide Coast Down Protection
First Generation Magnetic Bearing Compressor
Integral VFD
Permanent magnet
brushless DC motor
Shaft & impeller
Inlet Guide
Vanes
Heat exchanger
for motor cooling
(refrigerant cooled
motor/VFD)
Compressor
control module
Magnetic bearings
and sensors
Discharge Port
Suction gas
How Does this Compressor Handle a Power Outage?
• Motor becomes a generator
• Charges bank of capacitors
• After the compressor comes to a complete stop, the rotor de-levitates normally onto touchdown bearings
Second Generation Compressor Design
• Improved IPLV – Increased Unit Efficiency from 75 to 100% Load
• Higher Capacity up to 700 Tons
• High Efficiency Aerodynamics – Single stage, Shrouded Impeller
• Improved Drive train – Stronger, Lighter Magnetic Bearings & Rotor
• Higher Lift Capabilities – CHW Storage
– Higher Latent Load Applications
Second Generation Magnetic Bearing Compressor
Magnetic bearings
and sensors
Permanent magnet
brushless DC motor
(refrigerant-cooled)
Suction gas
Discharge Port
Inlet Guide
Vanes
Single Stage
Impeller
VFD and controls
contained in
external panel
ARI Standard for Part Load Analysis - IPLV
“Integrated Part Load Value”
% Load % Hrs ECWT (°F)
100 1 85
75 42 75
50 45 65
25 12 65
• 44°F LCHWT
Engineered for flexibility and performance |
State of the Art Performance
Capacity
Tons
Full load
kW/ton
IPLV
550 0.551 0.325
500 0.531 0.312
390 0.599 0.328
360 0.572 0.325
290 0.627 0.326
250 0.627 0.354
150 0.616 0.357
Designed to be Quiet
• Ideal for any sound-sensitive application: Education, Healthcare, Multi-
Residential, Offices, Churches, Performance and Conference centers
Tons A-weighted Sound Pressure, db (per AHRI Std 575)
100% Load 75% Load 50% Load 25% Load
150 75.6 72.4 68.7 68.0
250 81.6 78.1 74.9 73.4
290 81.6 78.1 74.9 73.4
390 83.3 82.5 80.8 77.0
500 82.6 76.9 76.1 77.9
Lowest Total Cost of Ownership
High Reduced Sustainability Lowest Total Costs
Efficiency Maintenance
+ + =
Oil-Free Design
• Compare to normal centrifugal chiller
– NO Oil heater
– NO Oil cooler
– NO Oil pump and starter
– NO Reservoir
– NO Oil relief valves
– NO Oil piping
– NO Oil Filter/Housing/Shutoff Valves
– NO Oil Sensors and controls
• Greater reliability
– “Fewer things to break”
• Reduced maintenance costs
Oil Free = Long Term Sustainability
“The negative effects of oil contamination can
result in added operating costs equal
to your original chiller investment”
Oil Contamination - ASHRAE Project 601
Ran
do
m S
am
ple
s
0 5 10 15 20
13% Avg
% of Oil in Refrigerant
Engineered for flexibility and performance |
Negative Effects of Oil
Data from ASHRAE Research Project 601
Designed for Maximum Efficiency
Oil management systems degrade chiller performance by clogging nucleate
boiling sights on the surface of the tubes
Evaporator
Tube Surface
Meeting LEED Requirements
• EA Credit 1 – Better Efficiency vs
Baseline Building
Energy Consumption
- 19 Points Available
• EA Credit 4 – Enhanced Refrigerant
Management
- 2 Points Available
Magnetic Bearing Chiller Summary
• Exceptional Part Load Performance
– Reduced operating cost, EAc1 LEED points
• Low Sound Levels
– Application flexibility
• Oil-free Design
– Increased reliability, sustainable performance, reduced maintenance